Begs the question why a 4mm² RFC is this because of volt drop over the circuit length as it is the only reason I have ever installed one
RFC is normally a 32A breaker
So 2 Kw still remains as the recommendation IMO
so if i had 2 X 1800W heaters could i connect these to one RFC that has only 5 sockets on it and has no significant load. so basically im asking is the 2KW combined or per fixed applianceAppendix 15 suggests that the 2kW limit is due to the current carrying capacity of the cable.
Having multiple general-purpose heaters in different locations is OK, if fits the diversity of loads that the RFC is suited to.so if i had 2 X 1800W heaters could i connect these to one RFC that has only 5 sockets on it and has no significant load. so basically im asking is the 2KW combined or per fixed appliance
Having multiple general-purpose heaters in different locations is OK, if fits the diversity of loads that the RFC is suited to.
Having them in the one location, or if they are unusually high duty cycle (like an immersion heater that can be on full for an hour or more, not cycling after several minutes like a typical thermostatic heater) would be pushing it.
It is 2kW per load, with a maximum assumed of 26A => 6kW (not the typical 30A fuse / 32A MCB, see Table 7.1(i) in the On-Site guide).This is the only part that concerns me. is it an overall 2KW or 2KW per load