Just completing the testing of a transportable catering unit.(chip van). Within the NICEIC REPORT I must complete,

a.MAXIMUM TOLERABLE FAULT CURRENT(is the same as PSCC)?

b.MAXIMUM TOLERABLE UPSTREAM ELI.(is this the same as Zs)?

If so how do I achieve these values when the Power Transformer/Generator is different at every site,or would this mean a report must be completed at every site,every time the catering unit moves.

This unit moves 3 times a week.

Thanks for your help.
 
I would suggest that maximum tolerable fault current refers to the maximum before damage occurs.
So if the connection is made direct into the unit's CU, which should be rated at 16kA, the maximum tolerable fault current would be 16kA.
Whereas if the connection is made via a plug and socket rated at 6kA, the maximum tolerable fault current would be 6kA.
This would be PFC.
The maximum tolerable upstream ELI would be the maximum Ze that the unit can be connected to and still allow ADS to be achieved.
For instance if yout unit just had lighting on a 6A type B MCB, the maximum Zs would be 7.67Ω. If the resistance of the unit's wiring between the connection point and the furthest lighting point was 1Ω, the the maximum tolerable upstream ELI would be 6.67Ω.
If however the unit had both lighting and socket-outlets, and the socket-outlets were protected by a 16A type B MCB, the maximum Zs would be 2.87Ω. If the unit's wiring was again 1Ω, then the maximum tolerable upstream ELI would be only 1.87Ω.
 
Last edited by a moderator:

Reply to Maximum tolerable fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top