bristolsparky

Hi All,

Wondering if any of you could help...

I am currently pricing up a Nursing home extension and the easiest method to get a supply including the cheapest is for me to run a 16mm 3 core SWA from the existing care home to the extension which is approx 85 metres. The supply will be fed from 3 phase DB via a EATON memshield 2 C63 amp MCB. I am worried that this rather long run will give me a higher ZS reading than what is permitable by the regs?

If this can't be done which my calculations suggest it is too far of a run then i will need to get western power to install a new supply.

Please give me your feedback lads!
 
What about the normal design methods of achieving a lower Zs ? What will be the Zs of your final circuits from this extension DB be as they will be a deciding factor along with volt drop.
 
What calculations have you done for this?
Off the top of my head I'd expect it to need something more like 25mm or 35mm to meet VD and Zs requirements on the final circuits
 
i used a calculator that comes with am tech but does not make sense to me but i completely get what your saying davesparks but i just think 85metres is ridiculous for any cable length... would you recommend a switch fuse with 63amp BS1361 or similar and possible 25mm 3 core due the length and potential voltage drop?
 
Without the max demand it's a bit difficult to say. If you take your max demand as 63A (given the fuse you suggest) then your voltage drop will be:

(85x63x2.9) / 1000 = 15.5V

so far too high.

Without looking at Zs tables I couldn't say if it would meet the regulations, but if you're using one of the cores as the earth then you have a resistance of 2.3mΩ p/metre for your R1+R2 which equals 0.196Ω for the 85m run, that gives you an indication of whether you'll meet Zs figures or not, but without any final circuit information (or Ze) it's impossible to say.

I'm not sure why you are contemplating 16mm Bristolsparky? Your max demand would have to be <28A in order to stay within voltage drop levels and thats without taking account of the volt drop of the final circuits.
 
Last edited:
So you are taking a 63 amp single phase load of a 3 phase db you may well course a large inbalance on load over the phases it may be beter to take a 3 phase supply over to balance out load and help with voltage drop do you know what is in the exstention ? Showers, cooker, laundry, or just a few lights and sockets
 

Reply to Maximum zs calculation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
260
dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
558

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top