One of my clients asked me if there was a maximum Zs value when it came to testing the Main incoming supply of a TN-S system, as i'm not fully sure my gut instinct was that it depended on the type of system.

Can someone assist me?
 
One of my clients asked me if there was a maximum Zs value when it came to testing the Main incoming supply of a TN-S system, as i'm not fully sure my gut instinct was that it depended on the type of system.

Can someone assist me?

Typical 'maximum' Ze values are TN-S 0.8Ω and TN-C-S 0.35Ω, however, these values are not guaranteed by the DNO who may provide supplies with higher values for operational reasons in exception circumstance.
 
The maximum value will also depend on the protective device used to protect the supply.
The maximum Ze for a 100A supply would be less than 0.4Ω.
A Ze of 0.8Ω would limit you to a supply somewhere between 45-60A depending on the protective device.
 
The maximum value will also depend on the protective device used to protect the supply.
The maximum Ze for a 100A supply would be less than 0.4Ω.
A Ze of 0.8Ω would limit you to a supply somewhere between 45-60A depending on the protective device.

I wonder how many electricians consider this limitation when conducting their installation tests?? More to the point, would a 19 day DI even be aware of the limitation??
 

Reply to Maximum Zs clarification in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
255
  • Question
Suggests yes, but doesn't prove it, not all imperial cables were tinned.
2
Replies
15
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top