K

KiltedSparky

Hi,

we have a 400A MCCB Bs60947-2 installed and the Zs reading measured at device is 0.2 ohms the manufacturer has listed the Zs value for this MCCB at 0.045 ohms , i have been informed by designer of circuit that because the Earth fault current is known to be 1537A he has just to tweak a setting on breaker which is setting the Instantaneous element to 3.5 X 400 =1400A and this will suffice does this mean that the we do not require to adhere to manufacturers tabulated values or is designer wrong

hopefully someone can advise :smiley2:
 
Hi,

we have a 400A MCCB Bs60947-2 installed and the Zs reading measured at device is 0.2 ohms the manufacturer has listed the Zs value for this MCCB at 0.045 ohms , i have been informed by designer of circuit that because the Earth fault current is known to be 1537A he has just to tweak a setting on breaker which is setting the Instantaneous element to 3.5 X 400 =1400A and this will suffice does this mean that the we do not require to adhere to manufacturers tabulated values or is designer wrong

hopefully someone can advise :smiley2:

If the device has an adjustable multiplier then the designer might be correct but it's no good measuring the Zs 'at the device' it needs to be measured at the extremity of whatever circuit it is supplying.
 
Apoligies IQ that was a typo , the Zs was measured at the sub mains panel which the MCCB was supplying .The only problem i can see with adjusting the multiplier to suit the measured Zs reading is that when a periodic is carried out in 5 years time, surely the company carrying this out will rely on the manufacturers published readings and fail this circuit as a CAT 1 fault.
 
The competence (or lack of) of any future inspector is not your concern, if the design is correct and the installation corresponds with that design then you have done your duty.
 
Just write a comment on any certification/documentation explaining the reasons for the settings.....Would also place a tamper proof sticker over the dials of the MCCB, should be covered then.
 
Just write a comment on any certification/documentation explaining the reasons for the settings.....Would also place a tamper proof sticker over the dials of the MCCB, should be covered then.

Thanks AC , very useful advice . We are going to obtain a letter from designer so that it can be inserted into file with test certs but we never thought about the tamper proof sticker, that as you say should cover us when periodic is due :)
 

Reply to Maximum Zs exceeds manufacturer recomendations in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top