Hello, can someone explain to me the 'rule of thumb figure' (0.8) when calculating max Zs value's from BS7671!?
Currently doing a PIR in a foundry where i measured the ambient temperature at 21 degrees at ground level, i bet you can add another 10 degree's higher up ...and that's on a good day. Anyway surely i don't need this 0.8 rule in this situation and i'll use the values given in the regs!??? Or should i be calculating the values myself!???

Thank You
Gaz
 
Last edited by a moderator:
on your cert. you enter the value given in brb. you hope to achieve a ZS value of below the 80% temp. corrected figure. e.g. 32AQ type B is 1.44 in brb. 1.15 corrected. the lower the measured value, the better.
 
The 80% rule is to allow for the higher resistance, when the conductor is at working temperature (70ºC).
 
Last edited by a moderator:
Zs values in the BRB are take at an operating temp of 70 C.

When your testing the circuit wont be at 70 C Obviously.

Copper has a coefficient of .004 per 1 degree.

So if your conductor is the same temp as your ambient lets say 20 C, we need to make an allowance for testing.

So 70 C - 20 C = 50 C so 50 x .004 = .2

If we take the Zs values as a factor of 1, then 1 - 0.2 = .8

So 32 amp type B mcm Zs at 70 = 1.44, at a conductor temp of 20 C we need to make sure the resitance is no more than 1.44 x .8 = 1.152 ohms.
 
Thanx.
Another question then ...where i'm working has above average ambient temperatures, do i need to factor this into my maximum Zs values!? Or is this just a factor that effects my Zs reading!?
 
The maximum Zs values as per BS7671 will remain the same whatever the ambient temperature.
You would apply any corrections to your measured value.
 
Thanx.
Another question then ...where i'm working has above average ambient temperatures, do i need to factor this into my maximum Zs values!? Or is this just a factor that effects my Zs reading!?

Well if you assume your conductor temp is the same as your ambient, so lets say 35 C

so 70 - 35 = 35 35 x .004 = .14

so 1- .14 = .86 so x the Zs values in BRB by 0.86.

Appendix 14 give you a method which is appropriate which also takes into account the load(operating temp may be lower)
 
your readings will be affected by the ambient temperature. they will be fractionally higher at 30deg. than at 20. the corrected values in the osg are determined so as to be acceptable at 70deg. in other words, say your Zs is 1.15 at 20, 1.44 at 70. it would be around 1.25 at 30.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Maximum Zs values and the rule of thumb
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
gareth020,
Last reply from
gareth020,
Replies
10
Views
15,718

Advert

Back
Top