havoone

for a TT system in domestic house with 0.2 disconnection time, with either mcbs or fuses. do i use the max Zs values in Tables 41.2- 41.4 which have 0.4 and 5 s disconnection times ? obviously depending on type of circuit.
 
My reading would be 411.5.4 rule should be applied (Zs x Ia <= U0). But also refer to 411.5.2 which says to prefer RCDs for protection. Maybe someone with more experience of TT systems can clarify.
 
In a TT, earth fault protection is mostly by way of an Rcd
You will be very unlikely to have a low enough Zs for those tables to apply
Rcds are the prefered option

Table 41.5 refers to Rcd rating and max Zs for TT
These are the values
 
ahh so when filling in a cert for a TT system the max ZS value to be entered is taken from table 41.5 . so for domestic most likely 1667 ohms. another question then. if im filling a cert for a Tns system say with 32A breaker and Rcd protection, which Table should i refer too. thank you
 
ahh so when filling in a cert for a TT system the max ZS value to be entered is taken from table 41.5 . so for domestic most likely 1667 ohms. another question then. if im filling a cert for a Tns system say with 32A breaker and Rcd protection, which Table should i refer too. thank you

Table 41.3
 

Reply to maximum Zs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
937
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
260

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top