Maz Zs as per bs7671. | on ElectriciansForums
Discuss Maz Zs as per bs7671. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
cagedanimal2010
Morning guys, (& girls)
quick one, i cant seem to find the max Zs's for bs3871's in the BGB.
any help would be helpful!!
Cheers.
Danny
as i=p/u says,if in doubt, work it out. type 1 2871 is equivalent to type b 60898.
i.e for 5A = 5 x 5 = 25A to cause operation so 230 / 25 = 9.2 ohms ,corrected of course.
That works for a B type 60898 - 3-5 xIn
BS3871
Type 1 - 2.7 to 4.0 x In
Type 2 - 4.0 to 7.0 x In
Type 3 - 7.0 to 10.0 x In
Type 4 - 10.0 to 50.0 x In
To apply these to the calculation above, use the maximum figure for the type you're calculating for.
eg 30A BS3871 Type 2
230 / (30x7) = 1.09ohms (maximum uncorrected value)
sorry, gary, i should have said similar, not equivalent. values for both types ae given in table 2D , red osg. these are corrected values.
I'm just going off a PDF I have for circuit breaker standards.
I'll have a look to see if I can host it online somewhere so you (and others) can have a look.
Reply to Maz Zs as per bs7671. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yes, probably overthinkig, thanks.
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...