Miniature circuit breaker (MCB) time-current characteristic has two specific points in the big-times area:
  1. 113% of MCB rated amps (current of non-tripping),
  2. 145% of MCB rated amps (current of tripping).

According to the standards and to the manufacturers catalogues:
- current equal or less than 113% will not trip the MCB in a period of 1 hour,
- current equal or greater than 145% will trip the MCB in a period of 1 hour,
- current in between of 113% and 145% may either trip MCB or not.

The question arises how to coordinate MCB and cable: should the cable long-term admissible current be greater than 145% of MCB rated amps?
In other terms the above mentioned feature of MCB (not to trip if less than 113%) makes me very uneasy about specifying cable cross-secion for 100% of MCB rated amps.

What do you think? Isn't it dangerous to size the conductor to 100% of MCB rated amps concerning the fact that MCB will not trip until 113% and may not trip until 145%?
 

Reply to MCB characteristics and specification of cable cross-section in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
233
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top