D

doglog

hello
I have been called in to inspect a DB that has been soaked in a flood. The board is now dry but the MCBs have a problem. If I put the insulation resistance tester across the MCB, even if disconnected from board and final circuit, with the switch in OPEN i.e. OFF position I get a reading of about 0.20 meg. and with the swith closed i.e.ON I, as expected, get 0.00meg.
I have found an identical MCB which wasnt affected by the flood ( brand new i think) and the reading across MCB in OPEN i.e. OFF position I get >200meg as you would expect and CLOSED i.e. ON 0.00meg again as you would expect.
My collegue has 'tested' these MCBs i.e. tried them out:rolleyes: and they seem to operate normally..even in OFF position there is no 'let through' of voltage as I would have expected given the 0.20meg reading:confused:
But I think the MCBs should be replaced as their integrity cannot now be guaranteed..
Has anyone come across this problem before??
Thanks for any help,
Doglog
 
hello
I have been called in to inspect a DB that has been soaked in a flood. The board is now dry but the MCBs have a problem. If I put the insulation resistance tester across the MCB, even if disconnected from board and final circuit, with the switch in OPEN i.e. OFF position I get a reading of about 0.20 meg. and with the swith closed i.e.ON I, as expected, get 0.00meg.
I have found an identical MCB which wasnt affected by the flood ( brand new i think) and the reading across MCB in OPEN i.e. OFF position I get >200meg as you would expect and CLOSED i.e. ON 0.00meg again as you would expect.
My collegue has 'tested' these MCBs i.e. tried them out:rolleyes: and they seem to operate normally..even in OFF position there is no 'let through' of voltage as I would have expected given the 0.20meg reading:confused:
But I think the MCBs should be replaced as their integrity cannot now be guaranteed..
Has anyone come across this problem before??
Thanks for any help,
Doglog


I agree i think that all affected MCB's should be replaced.
 
We dont test mcbs,we have to rely on manufacturers so,
I dont think any manufacturer would take responsibility for their continued use

Doing an insulation test across an mcb may not be a good idea,continuity yes but insulation maybe not
 
I would agree with Des on this.....try a low res ohmmeter and a continuity test, I/R may damage them.

For peace of mind I would replace them too.;)
 

Reply to mcb help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top