Hi Guys,
as I've just started full time testing I've ssen a few strange things.

Today I was doing yet anothe EICR and found 3 SP MCB thjat were "Locked ON"

I was told by the maintenance sparks that

"so the tenants don't tamper with the metering the MCB's were locked on"

(there were CT's around the incomers and seperate;ly the locked on MCB's supply ing the meters)

I suspect that it is against the regs, but a reg to use against this fault.

any ideas guys?

Richard
 
Not really a fault, tampering with a protective device opens a whole can of worms.
 
The operating actuator can be locked in the on position as it doesn’t prevent the trip mechanism operating. The problem comes when the consumer / tenant wants to isolate the supply, it’s no different to the meter room being locked.

Look at any DNO MV switch, all switch positions are locked, it doesn’t prevent the unit operating under fault.
 
The operating actuator can be locked in the on position as it doesn’t prevent the trip mechanism operating. The problem comes when the consumer / tenant wants to isolate the supply, it’s no different to the meter room being locked.

Look at any DNO MV switch, all switch positions are locked, it doesn’t prevent the unit operating under fault.

ok, That makes sense,
however the DB is an Merlin Gerin Isobar 4.
and as this DB has MCB isolators the tenant could disconect the load and the isolate the circuit.

the whole thing about stop people tampering with the metering is a bit of a mute point as the tenant is a housing assiation, and not a corner shop on the verge of being make bankrupt.

Thanks again for your replies guys

Richard
 
The operating actuator can be locked in the on position as it doesn’t prevent the trip mechanism operating.
Thanks for that. I wasn't sure - never thought about it.

The problem comes when the consumer / tenant wants to isolate the supply, it’s no different to the meter room being locked.
Not sure if you mean the meter room being locked is acceptable or not.

Noticed one yesterday (just a big cupboard) which has acquired a padlock.
I don't know who did it.
 
Last edited by a moderator:

Reply to MCB Locks in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top