F

fire

i have come across two showers in different houses where they have installed 32A mcb on a 9.5Kw shower. switched the shower on full and measured how many amps is drawing which was well over 32A but the mcb doesnt trip. any ideas as to why?
 
i have come across two showers in different houses where they have installed 32A mcb on a 9.5Kw shower. switched the shower on full and measured how many amps is drawing which was well over 32A but the mcb doesnt trip. any ideas as to why?

This is normal, have a look at the trip curves for the particular type of protective device in the back of the good book, and factor in your operating current.

From the info in the table and the current you are running at, you will be able to work out how long the shower needs to be on for to make the MCB operate in overload condition, not short circuit. It should disconnect within 0.4 second in short circuit conditions.

Cheers..........Howard
 
Last edited by a moderator:
Type B will pop at 3 - 5 times the FLC
Type C at 5 - 10 times
Type D at 10 - 20 times
So in the event of a S/C they should Trip within their rated times but will actually hold a lot higher load than they're rated for, for quite a while.
 
Last edited by a moderator:
1.13 all day for a type B 60898

so for a 32A thats just over 36Amps

So... if the voltage is for example 254Volts at the shower, thats nearly 9 & a 1/4 kWatts. Not quite sure what the 'current use graph' is for a shower but doubt it runs at full tilt all day.
 

Reply to MCB Not tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top