Installing 8.5kw shower which will pull 37 amps, looking at shower cu with rcd, but it comes with 50a mcb will it be ok to overrate or should I change the mcb to 40a.
You would be better of fitting a 32A as mcb should be the same as or lower than the current carrying capacity of the cable as your mcb is meant to protect the cable if I remember correctly thats for 6mm cable or as the post above
Chris
Chris
Hi
Ib should be less than or equal to In, and In should be less than Iz. Not In less than Ib...
Regards
Reply to Mcb rating shower in the Australia area at ElectriciansForums.net
Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Better off with the click prw213 as it has twin screw termination.