My shed is only 5 Meters from my house, i will run a SWA cable from existing consumer unit to a shed consumer unit which will have 3 circuits for Sockets,Light and a 7.5Kw shower unit all i need to know is will a 16 Amp MCB be sufficient for the socket Radial circuit for 4 Double sockets
 
My shed is only 5 Meters from my house, i will run a SWA cable from existing consumer unit to a shed consumer unit which will have 3 circuits for Sockets,Light and a 7.5Kw shower unit all i need to know is will a 16 Amp MCB be sufficient for the socket Radial circuit for 4 Double sockets
No 16 A far to small, 7,5 KW SHOWER WILL TAKE APPROX 32 Amps on it's own, needs it's own dedicated circuit, should not be connected to a socket radial circuit. what siz cable will you be using for the radial?
 
No 16 A far to small, 7,5 KW SHOWER WILL TAKE APPROX 32 Amps on it's own, needs it's own dedicated circuit, should not be connected to a socket radial circuit. what siz cable will you be using for the radial?
I think the OP said there will be 3 circuits in the shed, and the question might have been regarding one of them, the sockets circuit.
There are bigger questions though, since a shower means a water supply, which could mean extraneous things to bond etc, and could have implications on the size of SWA used.
There are actually quite a few complex design considerations regarding earthing and bonding. I'd highly advise you to get your plans checked out by someone qualified.
For the record, this work is notifiable work under part P of building regs as you are both installing new circuits and (by the sounds of it) turning the shed into a special location.
 
I think the OP said there will be 3 circuits in the shed, and the question might have been regarding one of them, the sockets circuit.
There are bigger questions though, since a shower means a water supply, which could mean extraneous things to bond etc, and could have implications on the size of SWA used.
There are actually quite a few complex design considerations regarding earthing and bonding. I'd highly advise you to get your plans checked out by someone qualified.
For the record, this work is notifiable work under part P of building regs as you are both installing new circuits and (by the sounds of it) turning the shed into a special location.

I think the OP said there will be 3 circuits in the shed, and the question might have been regarding one of them, the sockets circuit.
There are bigger questions though, since a shower means a water supply, which could mean extraneous things to bond etc, and could have implications on the size of SWA used.
There are actually quite a few complex design considerations regarding earthing and bonding. I'd highly advise you to get your plans checked out by someone qualified.
For the record, this work is notifiable work under part P of building regs as you are both installing new circuits and (by the sounds of it) turning the shed into a special location.
miss read the OP Tim my bad
 
50AMCB 10mm cable or 63A MCB and 16mm cable. all depends on the total design load. esp with a bloody hot rain bath
The shower is the only big thing being used. It’s for dog grooming the other things will be a single strip light some trimmers and a hair dryer. Was hoping to get away with 6mm SWA as I have some left over in the shed. But I will take your advice. Thanks for the help
 
Going 10mm 3-core SWA at least makes sure you can meet any TN-C-S supply bonding requirements, usually good to 50A MCB but that depends, of course, on the supply Zs.

Also be aware that any new circuit (or CU) is notifiable work in England and Wales under part P of the building regulations. It might be safer, cheaper, and easier to get someone registered with one of the schemes (NICEIC, NAPIT, etc) to sort it out, even if you do the donkey work of digging trenches, etc, for the cable to go in.
 
bear in mind that your sockets will be limited. the shower takes upmost of the 6mm capacity. personally, I'd fit a 3kW under sink heater to activate when you turn the tap on. dog's only need warm water for grooming. anything above 45 degrees is too hot.
 

Reply to MCB Size for radial socket circuit. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

  • Question
Why aren't you asking them?
Replies
5
Views
860
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top