I think the OP said there will be 3 circuits in the shed, and the question might have been regarding one of them, the sockets circuit.
There are bigger questions though, since a shower means a water supply, which could mean extraneous things to bond etc, and could have implications on the size of SWA used.
There are actually quite a few complex design considerations regarding earthing and bonding. I'd highly advise you to get your plans checked out by someone qualified.
For the record, this work is notifiable work under part P of building regs as you are both installing new circuits and (by the sounds of it) turning the shed into a special location.