Anyone know if the later Hager MCB's can fit as a direct replacement for the old L113's (5A cartridge fuse unit)??

Thanks
 
The busbar pattern is an always fit situation in my experience. Not so with the enclosures though........
[ElectriciansForums.net] MCB to replace Hager L113


(not my work btw)
 
Hum.. got a MTN 106 out of my store and the "body" of the unit was too deep and cover wouldn't have got back on.... so a call to Hager confirmed that the only one that will fit will be from their M106 (BS3871 version - retired in 1995) - so I got on of those to fit tomorrow!

Pickies for anyone interested:

[ElectriciansForums.net] MCB to replace Hager L113

[ElectriciansForums.net] MCB to replace Hager L113
 
Hum.. got a MTN 106 out of my store and the "body" of the unit was too deep and cover wouldn't have got back on.... so a call to Hager confirmed that the only one that will fit will be from their M106 (BS3871 version - retired in 1995) - so I got on of those to fit tomorrow!

Pickies for anyone interested:

View attachment 30721

View attachment 30722
Murdoch, i must apologise if i have given you duff information. Replaced 8 of these with rcds no problem, and the board was quite an age which is a little strange.
Sorry for confusion caused.

Buckfast
 
Murdoch, i must apologise if i have given you duff information. Replaced 8 of these with rcds no problem, and the board was quite an age which is a little strange.
Sorry for confusion caused.

Buckfast

No need to apologise.

I just thought I'd update the thread for others to use for reference as and when they do searches on this subject
 

Reply to MCB to replace Hager L113 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
896

Similar threads

You can get surge-protected 13A plugs such as this...
Replies
2
Views
316
M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top