Hi guys,

another stupid question for you I'm afraid...

Been looking at Appendix 3 of the BGB, protective device trip times etc.

Am I misreading the graphs by thinking that an MCB does not necessarily trip at all in an overcurrent situation?

Take for instance a 32A Type B (Fig 3A4) on a 4mm T+E radial. You could be drawing 40A for the maximum time on the graph (10,000 secs or nearly 3 hours) without tripping. I'm a little confused as to how the MCB is protecting the cable like this (as it's only rated for a maximum of 37A)

Excuse the stupid question, I'm desperately trying to get my head round this stuff!
 
Actually, I think I've worked it out...

Found the bit that says that the overcurrent device must trip within 1 hour at 1.45 times the rating of the cable.

I guess they take a safety factor into account when they wrote the current capacity tables...
 

Reply to MCB trip times in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

Similar threads

  • Question
word of caution, the federal electric breakers are old bits of kit. I have known them sometimes to refuse to turn back on if they are tripped or...
Replies
7
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top