Just a quick one on this, please excuse my ignorance, but surely if there was a L - N fault, then any discrepency between the two would trip the RCD. Again please excuse me if I'm talking bulls**t
L/N fault intermittent, short or low insulation is exactly that L-N, rcd look for earth leakage and as this isnt down to earth the rcd wont see it.
To note though in a L/N short circuit can sometimes trips the rcd but this is from my own assumption due to magnetic saturation of the device when the ampage can be in the 1000+ range for a split second until mcb trips and due to rcd looking at mA magnetic fields in normal use its plausable to me it will get saturated and activate.
 
Update.....

Been back over the weekend and can not find anything wrong with any terminations, connections, etc. IR test >1999Mohm. Split load board with 1 x 40a mcb on each side. Also tested RCD to make sure and all is good. So I turned to the shower unit itself....

Very very low water pressure at the shower head concerned me, especially when I raised the shower head above the unit and the water nearly stopped before going red hot and then the shower cut out (thermal cut out for element I think). MCB was still "on".

I told her to call the plumber back and do a pressure test at the shower end, then have the shower checked. It turns out that the pressure was indeed a little low but is not the main cause, the shower element is causing the MCB to trip so the plumber has replaced the shower and all is good so far.

Brand new gear causing all the problems, they dont make stuff like they used to!!!
 
Thx for update and as you said the thermal cutout was their to protect element but its continuous overheating and tripping will be the cause of the element failing and tripping mcb .... All down to the low water pressure, i suspect the shower lacks a pressure valve something missing on cheaper shower brands.
 

Reply to MCB Tripping.. Help !! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
167
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
897
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top