Darkwood
L/N fault intermittent, short or low insulation is exactly that L-N, rcd look for earth leakage and as this isnt down to earth the rcd wont see it.Just a quick one on this, please excuse my ignorance, but surely if there was a L - N fault, then any discrepency between the two would trip the RCD. Again please excuse me if I'm talking bulls**t
To note though in a L/N short circuit can sometimes trips the rcd but this is from my own assumption due to magnetic saturation of the device when the ampage can be in the 1000+ range for a split second until mcb trips and due to rcd looking at mA magnetic fields in normal use its plausable to me it will get saturated and activate.