Floody
-
Hi guys,
Ok, ill tell you where Im at with this question. Nothing to do with college, but its something ive just read in a Trevor Linsley book.
"MCB Type B to BS EN 60898 will trip instantly at between three and five times its rated current and is also suitable for domestic and commercial instaltions"
(text from book)
So for example, a lighting circtuit on a 6amp MCB, will need to pull between 18a and 30a for it to trip. Is this correct?
As I was under the impression that if the MCB went over over 6a, even in the slightest, it would trip.
Ok, ill tell you where Im at with this question. Nothing to do with college, but its something ive just read in a Trevor Linsley book.
"MCB Type B to BS EN 60898 will trip instantly at between three and five times its rated current and is also suitable for domestic and commercial instaltions"
(text from book)
So for example, a lighting circtuit on a 6amp MCB, will need to pull between 18a and 30a for it to trip. Is this correct?
As I was under the impression that if the MCB went over over 6a, even in the slightest, it would trip.