can any1 please explain to me the maximum tripping times on mcb's.....i have installed lighting and powerd outlets in a commercial job....everything in dado trunking....my lighting circuits are protected only by 6amp mcb no rcd.....been looking through the 17th and it states that a disconnection time of 0.4 seconds is required for 230v final circuits....i thought only an rcd could disconnect that quickly,or does an mcb disconnect that quickly olso?...cheers
 
The lower your Zs the more fault current. Time/current characteristics for 6A type B mcb is 30A so Zs needs to be less than 7.67
 
dyland22,
If you cannot understand and design your installations to be assured of this then it is doubtful that you are competent to undertake this work.
 
I am more than competent to design and complete the work,thank you very much...!!.. my zs values are well within range,worked out my cable sizes,volt drop... a simple answer of yes an mcb does disconnect in 40ms when zs values are within the amounts given in table 41.3 of the 17th would have been nice.. :yesnod: wots the point in having a table that gives a zs value for 5s and 0.4!!.. why not only 0.4!!
 
Got to agree with Paul on this one. If you have to ask the question then should you have undertaken the job?
 
I am more than competent to design and complete the work,thank you very much...!!.. my zs values are well within range,worked out my cable sizes,volt drop... a simple answer of yes an mcb does disconnect in 40ms when zs values are within the amounts given in table 41.3 of the 17th would have been nice.. :yesnod: wots the point in having a table that gives a zs value for 5s and 0.4!!.. why not only 0.4!!

Because Table 41.4 (5s disconnection time) is for distribution circuits or for a circuit not covered by 411.3.2.2
 
whatever boys...i am a fully qualified electrician...its only a simple question!!..looks 2me like you dont know the answer!!..i just answered it anyway so no worries...nice friendly people here tonight!!
 
NMc has given the best answer here.
Does it not say a disconnection time of 0.4s for any circuit over 32a? Not 230v.

Sent from my GT-I9100 using Tapatalk
 
No sh*t mogga...all i am saying is that if i use an mcb for distribution circuit it would be within the zs value so therefore comply with 0.4 disconnection time..so wot is the point of talking about 5s when 0.4 has already been acheived!
 
The people that have responded to your posts are generally really friendly and respected guys,0.4 is not 40ms its 400ms,0.4s is for final circuits uoto 32a,above that 5s is applicable,so if you have less than the max zs permitted by bs7671 then it would comply with disconnection times.the 40ms applies to 30ma rcds for 5x readings.
 
I am more than competent to design and complete the work,thank you very much...!!.. my zs values are well within range,worked out my cable sizes,volt drop... a simple answer of yes an mcb does disconnect in 40ms when zs values are within the amounts given in table 41.3 of the 17th would have been nice.. :yesnod: wots the point in having a table that gives a zs value for 5s and 0.4!!.. why not only 0.4!!
Are you, then why don't you know the difference between 400ms and 40ms?
Why don't you know that MCBs do not operate in 40ms?
Why don't you know that the instantaneous operating time for an MCB is accepted as being 100ms?
 
it says for any final circuit not exceeding 32A....and then in the table anything from 120v - 230v TN system disconnection time is 0.4 seconds.
 
Worrying is it not!
We are generally expected to be nice and help these Muppets on here take our work away when they are obviously incompetent.

I appreciate the forum ethic, but, why should we answer questions that should never be asked?

IF the OP had said, I have been asked to..., but I have never done so I am looking for advice... etc. then this is a different situation.

However to come on and say I have done this and I am competent and qualified etc. and I am this and that and the other, and ask such a basic question then as far as I am concerned they are not.
 
got my 400ms and 40ms all mixed up and started to question everything!...my mistake..sorry all...think il dye my hair blond tomorrow!!!!!!!!! :)
 
Very interesting banter

To to clarify my earlier post the 7.67 next the rule of thumb applied to ut so max Zs would be 6.136
 
If it's an NICEIC certificate, or one that asks for the maximum permitted by BS7671, then you would put in the unadjusted figures quoted in BS7671.
I believe ELECSA or perhaps NAPIT certificates, allow either the values in BS7671 or the adjusted values.
Of course the IET Certificates don't require this value.
 
Tsk Tsk Dylan, you have upset the Zs brigade by asking them a question that they think you should know the answer to.

If ever you need to be reminded how complicated these things like Zs, Ze, R1+R2, trip times and RCDs etc are, just have a look through the forums and see the amount of queries about them and the people falling over each other to give their opinion.

I have yet to meet the person who off the top of their head knows everything there is to know about this industry, sometimes people would be better to consider that before launching into a scathing reply.
 
Tsk Tsk Dylan, you have upset the Zs brigade by asking them a question that they think you should know the answer to.

If ever you need to be reminded how complicated these things like Zs, Ze, R1+R2, trip times and RCDs etc are, just have a look through the forums and see the amount of queries about them and the people falling over each other to give their opinion.


I have yet to meet the person who off the top of their head knows everything there is to know about this industry, sometimes people would be better to consider that before launching into a scathing reply.

some of the lads who replied know there stuff, ie tony, mogga, and a few others, who are willing to help others out some just want attention and sit behind there computer giving charlie big balls thinking they know everything, no one knows everyone back ground yet all they try to do is belittle everyone, im sure one of the mods have said before, if you dont like the Q thats being ask then move on to the next thread,

where all the love gone:sad:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
mcb tripping times...help fried my brain!!
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
dyland22,
Last reply from
james king,
Replies
28
Views
11,649

Advert

Back
Top