Hi guys

has anyone had this problem before ?

I changed a old board to a 10 way wylex with 2 rcds

the testing was all ok apart from the kitchen, so this was rewired.

Everything is back on all the testing is ok, however as the house
is empty at the moment went back and noticed the downstairs
ring off, thought was odd as I remember turning everything on. Switched it back on and 15 mins later the mcb trips.
Changed the mcb for another, stayed there for a couple of hours all ok switch everything on, all ok, then unplugged everthing again and left.

Went this morning and it had tripped again ! Hardly any load !Took off every socket and checked all ok apart from a fcu had a chunk missing out of the neutral, so fixed that and switched back in all ok at the moment will go back to house tonight to see if has tripped again, not had this problem before if trips again anyone god any ideas what it could.
be ??
 
Last edited by a moderator:
Hello mate

It only does two rooms and two hall sockets, fcu was for elec rad in toilet, which Is always off, it has also a tv on it a few lamps. Couple of other fcu for wall lights but there all off and got right fuses.

Everything is off and still trips ???? After a while not straight away, as I am not there not sure how long it takes maybe a few hours ?
 
I,d do an insulations test on the rad, maybe the is where the problem lies. If it is not an overload fault (as you said all loads are off) then it is more likely an intermittent earth fault.
 
I,d do an insulations test on the rad, maybe the is where the problem lies. If it is not an overload fault (as you said all loads are off) then it is more likely an intermittent earth fault.

It wont be an earth fault as the OP states RCD's are installed in the CU and it is the MCB tripping.
Disconnect all loads and do a L-N insulation test, a low reading would indicate a fault or a load somewhere on the circuit you have missed.
 
Tell me about it ! The mcb I changed was from my stock, so going to buy a brand new one and try that !

The rad is turned off and isolated from the fcu.

I have checked every socket which is only 9 and no probs. Very confusing !
 
Going by the descriptions you've given, I'd put my money on the L-N insulation breaking down somewhere in the circuit.

It would be unusual (although not unheard) of to have 2 faulty MCB's like that.
 
tricky one-

assuming replacement mcb is ok and no disturbing loads taking out the 'B' type

and no overload (unlikely)

i'd be inclined to switch on all connected loads- connect L-N together at board and check at 250v to earth as i seen a few odd things happen with L-E short circuits even with rcd protection if memory serves

L-N short circuit seems most likely though

and of course could be totally wrong:confused:
 

Reply to Mcb tripping ???? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
164
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
983
And fully tested it with an MFT obviously
Replies
9
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top