Hi chaps not been here for a while,
The last 3 nights the 32a mcb for the downstairs ring has triped but has been fine during the day with everything on ie. dryer, washer, dishwasher, fridge etc.
I just got up for the obvious, and its triped again (3 am) I changed the mcb this mornng and meggered he circuit and it was over 19.99 Mohm. It has got me stumped! Any idea's
Cheers
 
Unplug everything overnight (except the fridge and freezer) then try that. Turn off anything that is connected to the downstairs ring - for example boiler, etc - you can always plug them back in in the morning.

If that trips then its one of the things plugged in.
Do a PAT test on the fridge and Freezer checking for earth leakage.

Out of interest have you got an RCD installed on that circuit - if not you may have an earth leakage problem.


Just to let you know you have something creating a low resistance between the line and neural (i you got an RCD)/or earth (if no RCD)
Your getting something with a resistance lower than 14ohms.

You can always plug the fridge and freezer into an extension lead running from the upstairs ring (if on a different circuit)

Good Luck
 

Reply to MCB tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
764

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top