jobber

i install street lighting, i use lucy cut outs at the origin then mcb's feeding my 6 flood lights at the top, they are 3 phase, a new lad in are work has been getting rid of the lucy cut outs and putting single phase mcb's in at the origin, i think that is wrong. what do you think
 
the mast has a 3 phase supply, the 6 400w flood lights are split with 2 lights per phase, the mcb's that are being installed by the other lads are single phase mcb's.
 
the mast has a 3 phase supply, the 6 400w flood lights are split with 2 lights per phase, the mcb's that are being installed by the other lads are single phase mcb's.

ideally you want a 3 phase breaker as the supply to the light posts originate from a 3 phase breaker otherwise if a single mcb trips you would then have an un-even load at the 3phase supply end which is not ideal really.

either way it shouldnt cause any real problems - but i would prefer to keep them on 3 phase mcb's.

im sure someone can confirm this.

thanks
 
We always provide Lucy, or Lucy style cut-outs prior to any single phase protection, on all our pole street or area lighting. And some of our poles have far more than 6 fittings....

So i'm with you jobber!!!
 
ideally you want a 3 phase breaker as the supply to the light posts originate from a 3 phase breaker otherwise if a single mcb trips you would then have an un-even load at the 3phase supply end which is not ideal really.

either way it shouldnt cause any real problems - but i would prefer to keep them on 3 phase mcb's.

im sure someone can confirm this. thanks


I would think the last thing you would want, is a single fault on a single fitting, taking out the whole pole!!
 

Reply to mcb's at origin in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

@DefyG is right... I'm not fully sure what your boss is after as when doing single line diagrams I usually show the whole installation. Anyhow I...
Replies
4
Views
386
  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
433

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top