Anyone know of or where to find Max permitted Zs for mccb`s (60947-2) please?
The max trip current (Im) for this type of MCCB is 800 A and if the nominal voltage (Uo) is 230 v, then max Zs will be Uo/Im = 0.2875 ohms.
You are always safer using manufacturers data on these devices, many have adjustable characteristics on the curve.
Exactly!! .... The data sheet that comes with these MCCBs will generally give you this information. If it doesn't, then it will direct you to a web site page that does. Generally all MCCBs will have different Max Zs even those of the same manufacturer, between different model numbers in the same frame size....
im struugling to find max zs readings for siemens breakers if anyone could help, cheers
Struggle no more, contact Siemens with the exact MCCB details, and they will furnish you with the information!!!
As i have stated above, Even MCCB's of the same manufacturer and frame size will/can have very different Max Zs requirements...
Amtech have a handy device called "single cable" which has almost all MCCB max Zs values for anyone that is interested
Interesting!! ...Any chance of showing a list of Schneider MCCB's with their max Zs values. I'll check them against my home made data base. ...Iv'e a feeling this list isn't going to be too accurate to be honest!!
Its not in simple tabulated layout form its has selection process where you choose the make, family, type, protection and rating then it calculates it for you. But if you have yours in tabulated form i'll happily check them against what amtech says.
you mean its not precise to 4 decimal places ??
tut tut , next you'll be rounding pi down to 3
;-D
You may scoff, but there are significant differences in MCCB maximum Zs values attached to different types, even within the same type and frame sizes and families of the same manufacturer. Were not talking about type tested MCB's here... lol!!
Reply to mccb max Zs ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Useful to know. In my case there will be 150x150mm trunking at top/bottom and almost certainly I will be using tri-rated cable, probably 70mm...