Does anyone have any Ideas why a 125A mccb would trip?
Been called out today twice to same job 1st time I reset it and no problems ,but then it went again this evening .
It's not overloaded ,I didnt do any IR tests as I couldnt gain access to the bar It was suppling just the office.
My first thoughts were a damaged sub main but I cant think were as there has been no major work there for a month .
I did notice the mccb was very warm but there were no loose conections.
I know what I have to do to find whats wrong but am looking for ideas to help speed things up.
Thanks in advance.
 
yip
L1 -11a
L2 -25a
L3 -30a

Phases are a bit unballanced but thats another issue this has been running like this since it was done 4 years ago.
 
Its a damm funny set up .The mccb is in a panel board and feeds through a meter to a set of iscos from which there are 3 switchfuses feeding sub boards.
One db for the office another for the bar and another for the niteclub.
I havent been there to check the full load when the bar and niteclub are both in operation but the mccb is tripping when there is virtualy no load on it which to me seams like a damaged sub main.
Have any of you had a problem like this and it turned out to be a circuit of one of the sub boards?
I cant see this really happening as the mcb/rcbo should be protecting its own circuit!

It has a kitchen ,as far as I know its all gas. Bar wasnt even open today so only thing running is fridges and stuff,there would be dishwashers and glass washers but the wouldnt have been running today.
 
Last edited:
If it had been a fault that was occurring on one of the circuits on the dis boards the individual breaker would have gone not a 125A mccb. It sounds like it could be an overload especially with the mccb running hot and bars and clubs are buggers for adding on stuff,or a lose connection at the dis boards in the club or bar, but as you say you'll find it pretty quickly, may even be a faulty mccb. Does the mccb have a thermal overload or short circuit setting .
 
Last edited by a moderator:
sorry mate .
A panel board that accepts mccbs, its just like a normal tp&n board only on a large scale and designed for mccbs.
the meter is seperate and fed from an mccb in the panel.
hope this describes it better ,thats the only name I know for It
 
Check the discrimination on all the ocpd's , I had a simular problem a year ago, faulty overdoor heater protected by type d mcb.
 
I had something similar a while back. It turned out to be the bars in the 3phase DB tracking and then clearing due to moisture build up in the kitchen through cooking steam ect. I found it eventually when the DB go bang, because everytime it was tested everything was clear and nothing to see.

Just an idea ?
 

Reply to mccb tripping in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K
I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top