horticultral lighting circuit - 14 x t/p 16A mcb's each mcb has 6 x 600w 400v son lights, fed from a contactor which is fed by a 160A merlin gerin mccb. across the contactor measures L1 - 130A L2 - 133A L3 - 132A but after 6hrs the 160A trips. any ideas ? there is another 2 identical systems in the same cabinet working ok. system has worked ok for last 12 months.
 
I have only seen these on youtube but from that have managed to get a grasp of what they are about but i would like more knowledge of them so i will be sure to ask the lecturers about them at college.....
 
Can't get onto the website!!!! What have you checked so far mate? Do you own an Amp Meter, and measured the actual current draw from these fittings? MG MCCBs are generally good very reliable units, but like everything else they can fail. You may very well have a unit where the adjustable element is U/S... Before anything else check those light fittings, one or more may have a ballast or starter that is in the early stages of going down!!!
 
I have only seen these on youtube but from that have managed to get a grasp of what they are about but i would like more knowledge of them so i will be sure to ask the lecturers about them at college.....


Have a look through the PDF, page 14 onwards has info on 60947-2 MCCB's.
 
I have only seen these on youtube but from that have managed to get a grasp of what they are about but i would like more knowledge of them so i will be sure to ask the lecturers about them at college.....


Go onto the MG website, they have some very good reference material, it will probably tell you a lot more than your lecturer at collage. It obviously based on MG equipment, but it will be generally the same for all manufacturers MCCBs, ACBs, GCBs, etc. That's if you can get onto there website!!...lol!!
 
there 84 units on this mccb. The Amps are roughly the same as the 2 other mccb 's next to this one. Putting on one mcb and measuring at mccb at a time all 14 mcb's are the same.
 
There is one sure way to find out if you have a dodgy MCCB and that is to swap it over with one of the others. If the fault transfers to the other circuit, it's down to a new MCCB unit!!


Is it possible to swap with one of the other units on this installation??
 
If it runs for several hours without tripping then it's not really the kind of fault I would go after with a thermal imager. Maybe a current logger would be a better weapon of choice.

Am I right in assuming that none of the t/pole 16A MCB's are ever tripping along with the 160A main breaker?
 
Have you checked the lugs and bolts on the connections top and bottom, If they're getting warm enough to cause nuisance tripping you would feel it by hand after the system has been running a while if you isolate the power. There would probably also be tell tale signs of heat on the pvc insulation near the lugs.

Otherwise as engineer54 suggested try swapping out the breaker with an identical one from another system to prove if it's faulty. I have to say though that Merlin Gerin equipment is pretty damn reliable, I'd bet my lunch it's not a faulty breaker.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
mccb tripping
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
23
Unsolved
--

Advert

Thread statistics

Created
dave-gardiner,
Last reply from
Marvo,
Replies
23
Views
2,830

Advert

Back
Top