Hi chaps,

Been asked to sort a nuisance tripping issue, which I've narrowed down to what I think is a faulty RCD (trip time varying between 45ms and 260ms at random for the same 1x30mA test).

Board is MCG branded and the local wholesalers don't stock their stuff? I'm assuming it's a rebrand of someone elses kit, anyone know whose?

Cheers!
 
Ramp test shows tripping at 21mA.

Asides from the unit tripping at vastly differing intervals as stated, a couple of times when I went to reset it the switch failed to engage and sprang straight back down again.

Do you know which other brand units would be a straight swap?
 

Reply to MCG consumer unit... RCD needed! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top