Discuss Measured Loop impedance in the Australia area at ElectriciansForums.net
On another issue how do test the loop impedance at a fixed appliance or a light, to fulfill the measured loop impedance column requirement on the schedule of tests. will the calc R1 + R2 suffice?
Measure Ze at the supply terminals and add R1+R2, the result is inserted into the Zs column. There is no doubt that a live Zs reading at the switch or light is best but we are allowed this method - see Guidance Note 3.
Ooooh. I wouldn't bet on it.They probably figured it out in the four years since this question was asked.......
oh do you?take down the ceiling rose and test. with the rcd's now you will need a no trip tester
Reply to Measured Loop impedance in the Australia area at ElectriciansForums.net