Amp David

-
Mentor
Arms
Did a Zs on a lighting circuit today and the value was less than my calculated value.

Haven't got my note to hand so can't give the exact figures. Thought it could be supplementry bonding somewhere, but there isn't any.

Can anyone shine a light on the matter:(
 
could be supp. bonding hidden from view somewhere, boxed in? as long as it's a good reading, and not too far from calc. job's a good 'un
 
yes lenny spot on will have a lower value beacause of the parlell earth paths from the main protective bonding conductors
When you calculate from Ze + (R1+R2) this doesnt so will give a higher value than the measured value
 
yes lenny spot on will have a lower value beacause of the parlell earth paths from the main protective bonding conductors
When you calculate from Ze + (R1+R2) this doesnt so will give a higher value than the measured value

Any paralell path will affect all circuits you test, but its only on the lighting circuit that figure are vastly different??
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Amp David

Mentor
Arms
-
Joined
Location
Glossop

Thread Information

Title
Measured Zs up the swanny?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
Amp David,
Last reply from
Jimmy Boy,
Replies
8
Views
1,287

Advert

Back
Top