measurements on a three phase distribution board | on ElectriciansForums
Discuss measurements on a three phase distribution board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
cocko75
hi can you anyone help i had to undertake measurements on a simulated 3 phase distribution system it had main switch, bus bar then went to 3 sockets we had to take test with all the sockets on and then turn one off and test it all the readings where different L1 L2 L3 and n (3kw) L1 4.87 L2 4.95 L3 4.86 and n 0.2 all sockets on L1 4.84 L2 5.00 L3 0.00 N 4.95 one socket off . do you have an explanation off the difference between the measurements recorded many thanks would be greatful if you had the answer :confused:
Reply to measurements on a three phase distribution board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
5K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.