Dear all,

I have what I hope isn't a silly question, I have a circuit on my CU that powers the spark ignitor for the gas hob, the inner workings are obviously all tucked away and pretty inaccessable, to that end how would I measure the resistance, should I measure from the CU end by disconnecting the line and neutral from the breaker (practicing safe isolation obviously) and measure from there

Thanks for any help.

Down2earth
 
Hi D2E,

I would disconnect the particular circuit from the c/u, connect phase and CPC in a connector block, Null your test leads, go to hob connections (L-N-E) and test between L-E) Or Live and metal casing of Hob. With the Hob isolator on of course.

Hope this helps.

WTP
 
Hi D2E,

Yes you could do that although when testing r1 r2 of a circuit the r1 r2 of the apliance should not be taken into account. Therefore you should realy disconnect the cable from the cooker altogether and then test.
 

Reply to the thread, titled "Measuring r1 and r2" which is posted in Australia on Electricians Forums.