L

lewismogwai

Hi all, I've just put in a new 32amp ring main in a domestic Crabtree Starbreaker box , I've tested for R1 + R2 at all of the 12 sockets in the ring (a loft conversion) and I'm getting 0.36 as the highest reading.

When I test for ZE I'm getting 1.28 which when I add this to R1 + R2 I'm getting a reading of 1.64 for ZE, which of course is too high to make the maximum earth fault loop impedence in ohms against BS7671:2008 (2011), which specifies a value of 1.16, which of course needs to be adjusted down to 0.92 to comply.

Any ideas as to how I can put this right? Is my ZE abnormally high and would you say that my R1 + R2 is on the high side?

Any help much appreciated.
 
32A MCB type B is 1.44 adjusted to 1.16. your Ze is excessive both for TNC-S and TN-S. if it's a TN system, call DNO.
 
What earthing system do you have ? What's the max ZE for your system ?
There's your answer.

You know what, as I didn't put the board in I didn't think there was a standard for this, as it was all down the measurement on the circuits coming off it - I'l have a look thanks.
 
Its a Crabtree Starbreaker - lts got a 63A 30mA RCCB on it for earth leakage protection, to go with the MCB's - Type B BS EN 60898 - with the load split between upstairs and downstairs.
 
Hi all, I've just put in a new 32amp ring main in a domestic Crabtree Starbreaker box , I've tested for R1 + R2 at all of the 12 sockets in the ring (a loft conversion) and I'm getting 0.36 as the highest reading.

When I test for ZE I'm getting 1.28 which when I add this to R1 + R2 I'm getting a reading of 1.64 for ZE, which of course is too high to make the maximum earth fault loop impedence in ohms against BS7671:2008 (2011), which specifies a value of 1.16, which of course needs to be adjusted down to 0.92 to comply.

Any ideas as to how I can put this right? Is my ZE abnormally high and would you say that my R1 + R2 is on the high side?

Any help much appreciated.
Have you nulled the leads? As everyone else has asked what is the earthing arrangement?
 

Reply to Measuring ZE - Am I getting too high a measurement? - what is 'normal range'? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top