semaphore
Hi guys,
We were testing an install the other day with a new meter megger 1553.
Ze is a LIM as we cannot disconnect earthing
Could not test IR on this circuit due to electronics connected.
Did long lead R2 but it's all conduit with no separate CPC and no fly leads at accessories but has plastic fittings. Then tried Zs but it comes up on display as "Trip" and does not give a reading but does not actually trip the 10A 3871 type 3 breaker
Went and got old Fluke 1652 from van but it's out of calibration and tried it with that using the 3 leads but still no joy.
I assume it will not give a reading as a safety measure as the touch voltage may rise too high due to poor insulation resistance? But this is just a guess. I can't find any documentation on this.
I have now emailed Megger but they have not got back to me. I just thought someone on here might know. Cheers
We were testing an install the other day with a new meter megger 1553.
Ze is a LIM as we cannot disconnect earthing
Could not test IR on this circuit due to electronics connected.
Did long lead R2 but it's all conduit with no separate CPC and no fly leads at accessories but has plastic fittings. Then tried Zs but it comes up on display as "Trip" and does not give a reading but does not actually trip the 10A 3871 type 3 breaker
Went and got old Fluke 1652 from van but it's out of calibration and tried it with that using the 3 leads but still no joy.
I assume it will not give a reading as a safety measure as the touch voltage may rise too high due to poor insulation resistance? But this is just a guess. I can't find any documentation on this.
I have now emailed Megger but they have not got back to me. I just thought someone on here might know. Cheers