Megger MFT 1553 | on ElectriciansForums
Discuss Megger MFT 1553 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I
ICE
Hi Guys and Girlies,
Looking for advice on using this meter (Megger MFT 1553) for doing EET to find resistance of earth rod on a generator. looking for Ω and Ka.
Hi
Firstly some generators have a ' phase and neutral ' output with a separate earthed chassis, the others have a ' phase and neutral ' output with either the earth connected to neutral or means to allow this connection.
The former will require a dedicated 3 terminal earth electrode tester to test the electrode while the latter can be tested with a loop tester.
For this test the MFT should be switched to Hi loop and the red and earth test leads should be connected.
Remember that if there is no neutral earth connection there will be no loop so no test. A simple dead continuity test between neutral and earth will comfirm this after safely locking out the generator.
Regards
Megger TSG
Reply to Megger MFT 1553 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
I've discussed this with the OP directly as we are friends, but for anyone searching in the future, the service manual suggests that this...