Megger MFTs display PFC directly on the three lead no-trip loop test and therefore it is not necessary to test for PEFC and PSCC separately and select the highest reading for PFC. They do this by injecting a current pulse of <30A L-N for the PSCC loop and injecting a current pulse of <15mA L-E for the PEFC loop. The Megger MFT repeats this sequence 6 times, storing the readings in memory as it goes, on completion of the test it averages the 6 PSCC and 6 PEFC results, selects the highest average reading and displays this as the PFC. The reason for doing this is to maximise the noise immunity of the test. It is for this reason that Fluke fans often criticise the Megger MFTs as having a slow no-trip loop test, however, Megger users rarely, if ever, get a no-trip loop test inhibited and a noise warning displayed, unlike the Fluke MFTs.
From the explanation of how a Megger MFT does it's no-loop testing I think it's obvious to see that the L-N PSCC loop may well trip a particularly sensitive 6A MCB.
Because the <30A pulses have fast rise time leading edge with a peak current of hundreds of amperes it is essential that fuses used in the probes or meter are High Rupture Current (HRC) rated.
From the explanation of how a Megger MFT does it's no-loop testing I think it's obvious to see that the L-N PSCC loop may well trip a particularly sensitive 6A MCB.
Because the <30A pulses have fast rise time leading edge with a peak current of hundreds of amperes it is essential that fuses used in the probes or meter are High Rupture Current (HRC) rated.