Megger MFT1553 unusual readings while testing rcbo's | on ElectriciansForums
Discuss Megger MFT1553 unusual readings while testing rcbo's in the Electrical Tools and Products area at ElectriciansForums.net
leebut
Bury
Hi Guys
I'm fresh to the EF had a bit of a bad day, replaced an old wylex Bs3036 consumer unit with a new enclosure with 8 Rcbo's (1 x 40, 4 x 32,1 x 20, 2 x 10 amp) all went in fine all continuity, end to end tests and insulation tests went well, until I started testing the rcbo's using the auto rcd test on my MFT1553 all eight circuits tested the half load fine (>1999) but as soon as test two started the Megger gave me a reult of 400ms and wouldnt test any further.
I then tried testing all eight circuits again manually, on 1 x it's result were 400ms, then at 5 x the result was 40ms both tests did not trip the Rcbo's i then carried out a ramp test on all the circuits they all tested at 51ma, I have tried brand new batteries but I'm getting the same results, I took the tester home and tried it again on my house with exactly the same results, has anyone had the same problems and how did you get the tester back on track??
many thanks
Lee
i was testing at the Rcbo's but i even tried testing a socket outlet both onsite and at home all with the same results
lee
i was initially using the two leads directly onto the Rcbo's at the DB then tried testing at socket outlets with same results
lee
Hi Lee,
I've had a quick word with one of our engineers in our service department, if your tester is doing the same thing on different circuits, it's possible it's not putting the test current into the circuit and the unit is simply timing out - the unit should be returned for investigation. These models carried a 3 year warranty, so depending on the age, it may still be covered.
When you turn on your tester look at the screen it will briefly show a code then it will flash up with your battery voltage. New batteries should show more than 12 volts on the screen! On the 1 x and half I would of said you had the blue scale set at 10 mA but putting 50mA in on the 5 x should of tripped the RCD. The 51 mA ramp also says something about your meter I take it the RCBO did trip. Let us know how you get on !
I have this tester, batteries are not great in it. I it reads 9.? Or less I get funny results all the time. Have learnt to carry spare batteries at all times. I have never had trouble testing rcbos though. This definitely sounds like u need to send it back and be checked.
Reply to Megger MFT1553 unusual readings while testing rcbo's in the Electrical Tools and Products area at ElectriciansForums.net
Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
TerryBNZ
T
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...