if its overloaded, then it sounds like its running just under its tripping current, or the conductor is too small to carry the overload current. maybe the In setting is set too high for the cable. just guessing here !
 
Did they fit a new breaker, or just refurb the old breaker?? Did those that fitted the breaker last, thoroughly test the circuit it was supplying?? Did they do load checks, before setting the breakers protection/tripping perameters?? And last but not least..... was this breaker the withdrawable type, and if it was did they check the contact resistance between breaker and switchboard contacts when the breaker was in the fully inserted position ???


Other than that, it would indeed be reasnable to suspect loose bolted connections onto bus bars or cable(s)....
 
Come across a 400a main switch that was burnt out .all connections tightened by king kong I reckon.Stretched all the bolts so the connections were actually looseYou picture the result. Torque wrench required in the first place
 

Reply to Melted mains circuit breaker in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
184
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
561
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

Sort of; technically speaking the 10mA is required to hit the 40mS target at 50-149mA, whereas the 30mA device can be happily snoozing along for...
Replies
8
Views
780
Given the apparent lack of earth, combined with no short circuit or over current protection, I'd contend that luck has been the sole factor...
Replies
5
Views
558
nicebutdim
N

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top