Melted Plug and Socket cause | on ElectriciansForums

Discuss Melted Plug and Socket cause in the UK Electrical Forum area at ElectriciansForums.net

zerozero7

DIY
Joined
Jul 7, 2020
Messages
9
Reaction score
1
Location
North West
Hi all,
Washing machine plug and socket melted around Neutral pin. Whilst removing socket faceplate, noticed one brown wire was not in the terminal. May have come out of the terminal when pulling the socket forward or may have been out all the time.
Is this lose or disconnected live cable the 'definate' cause of the overheating on the neutral pin?
Thanks, Gary



[ElectriciansForums.net] Melted Plug and Socket cause



[ElectriciansForums.net] Melted Plug and Socket cause
 
If the loose live wire was causing a problem, the heat damage would be showing around that terminal.

I think this has been caused be the neutral socket not having a good grip on the plug pins.
It can happen with older sockets, or ones that are plugged/unplugged constantly.
Can also happen if the sockets have had those plastic “child safety” shields fitted
 
That looks like the contacts between the plug and socket were not making proper contact.

It could be an undersized plug (cheap China incorrect size)

It could be oversized socket - poor quality socket (BG) or having an oversized plug inserted previously -- typically the ridiculous "child safety" things that reduce the safety, but the public uses.

It could be corroded contacts - usually the plug as the brass contacts get wet and go green, especially with stuff near washing machines, in garages etc.

Although the incoming connection may have been loose that actually wasn't the cause here - it does show that you probably need to get the installation checked properly though.
 
That looks like the contacts between the plug and socket were not making proper contact.

It could be an undersized plug (cheap China incorrect size)

It could be oversized socket - poor quality socket (BG) or having an oversized plug inserted previously -- typically the ridiculous "child safety" things that reduce the safety, but the public uses.

It could be corroded contacts - usually the plug as the brass contacts get wet and go green, especially with stuff near washing machines, in garages etc.

Although the incoming connection may have been loose that actually wasn't the cause here - it does show that you probably need to get the installation checked properly though.
why knock BG .I fitted loads, never any problems.
 
why knock BG .I fitted loads, never any problems.
So have I

But it isn't the best quality, and I probably wouldn't use one where it was subject to large loads such as a washing machine/dryer or where it would be plugged in/out a lot.

I have them in my own bedrooms and living rooms etc - to be fair mostly the usb versions, but within the kitchen and utility where there will be kettles and fryers plugged and unplugged and for the dishwasher and washing machine, I have used more premium examples.
 
we got kettle (3kW) and micro (1kW) in a double BG with usb. been in 6 years, no problems. in garage, washer, tumbler, 3 freezers all in 2 x BG doubles, extension lead for freezers.
 
Hi all,
Washing machine plug and socket melted around Neutral pin. Whilst removing socket faceplate, noticed one brown wire was not in the terminal. May have come out of the terminal when pulling the socket forward or may have been out all the time.
Is this lose or disconnected live cable the 'definate' cause of the overheating on the neutral pin?
Thanks, Gary

Hi Gary

Had the brown (Live) wire not been present you wouldn't have got much washing done ?.

The fact that it came out when withdrawing the front plate definitely indicates it wasn't tightened properly in the first place, and you have a cr@p installation.

So long as the wires aren't burned back beyond trimming distance this is no big deal. Just buy a decent quality new socket and replace it. Ditto a decent plug for the flex.

It might be worth gradually going round all your other sockets to check terminal tightness as well (switch off at the board first!). There's a bit of craft in getting the torque right - it should be firm, but not torqued down like the wheel nuts on a 44 ton truck! All that does is to strip the threads and/or cut through the copper cable.

Cheers and good luck, Mark.
 
Thanks all
Hi Gary

Had the brown (Live) wire not been present you wouldn't have got much washing done ?.

The fact that it came out when withdrawing the front plate definitely indicates it wasn't tightened properly in the first place, and you have a cr@p installation.

So long as the wires aren't burned back beyond trimming distance this is no big deal. Just buy a decent quality new socket and replace it. Ditto a decent plug for the flex.

It might be worth gradually going round all your other sockets to check terminal tightness as well (switch off at the board first!). There's a bit of craft in getting the torque right - it should be firm, but not torqued down like the wheel nuts on a 44 ton truck! All that does is to strip the threads and/or cut through the copper cable.

Cheers and good luck, Mark.

Hi Gary

Had the brown (Live) wire not been present you wouldn't have got much washing done ?.

The fact that it came out when withdrawing the front plate definitely indicates it wasn't tightened properly in the first place, and you have a cr@p installation.

So long as the wires aren't burned back beyond trimming distance this is no big deal. Just buy a decent quality new socket and replace it. Ditto a decent plug for the flex.

It might be worth gradually going round all your other sockets to check terminal tightness as well (switch off at the board first!). There's a bit of craft in getting the torque right - it should be firm, but not torqued down like the wheel nuts on a 44 ton truck! All that does is to strip the threads and/or cut through the copper cable.

Cheers and good luck, Mark.
Thanks Mark...
"Had the brown (Live) wire not been present you wouldn't have got much wasting done ?"
It must have been using the other Brown ?
Not sure where the second lose brown looped to but the as far as I know all the other sockets were working so it was probably still in the terminal until I pulled the faceplate away although it was obviously poorly gripped.
Gary
 
It's quite probably a ring final circuit (32A MCB?), so is intended to be fed power from both cables. On a well loaded circuit, this can cause damage to the fixed wiring, all the way back to the fusebox.
 
Thanks all for great prompt replies.
Only 1 year old good quality (?) BG socket with good quality (?) factory fitted washing machine plug. Permanently plugged in so socket has little use and located in a dry kitchen cupboard adjacent.
Seems to make sense that if it was a poor contact in the terminal there would be more heat damage in that location but as the damage seem to be around the socket and plugs prong, I am guessing it was a poor connection in there.
Got a very nervous homeowner who thinks her house is going to burn down and my ""probably a lose connection"" just isn't good enough.
Arranging for Spark who done the kitchen install to come back and give it the once over to reassure her.
Gary
 

Reply to Melted Plug and Socket cause in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

In the picture of the socket, it looks like one of the neutrals may have been screwed in over the insulation. Therefore, the live may also have...
    • Like
Replies
14
Views
671
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K