Afternoon, had a fault this afternoon at a property that one of my lads rewired 12 month ago. The property in question has a 11 kw in line heater that warms a tank up for the domestic hot water and also the central heating. The heater draws close to 50 amp so we fitted a separate consumer unit, tails, henley block ect. The rcd was a Wylex 80A 30mA with a 63A type b mcb. The circuit is wired in 16mm t+e all surface mount and no signs of burning on the cable ect. The problem that I have is this afternoon I have fitted a new rcd consumer unit (Schneider electric) with again a 80A rcd 30mA and 63a mcb fitted. After half a hour I started feeling heat on the rcd and the smell of burning. I have isolated and had to remove as needing to think what is causing the heat. I made sure that all the connections were tight. The voltage of the install is 243V tncs. Have the amp meter on and is only drawing 46A so it's not overload. Any one got an idea of the cause of the burning. Hope you can help, thanks Danny
 
Where have I put that ?

And the Wylex on totally melted and the new Schneider one started to melt after half a hour but only drawing 47A I just don't understand .
was in reply to RCD testing mate as in mA....not rated amps capacity.... bad contacts as eng says inside and you said all terminations tight....did you retighten em after you brought/banked the cables into position as stranded can come loose again after being manipulated......
 
Have you got the ends IN the termination clamps on the rcd or BEHIND em? can happen this ....especially if its been a long day....seen it a few times at places we`v been to where the rcd either wont stay in or theres evidence of scorching on mcb terminations etc......
 
Last edited by a moderator:
test the circuit insulation etc and increase the curent of the RCD , although the current drawn is below the rated current if the contacts are slightly weak then it can over heat at high currents , i would always go for the higher rated RCD in situations like this so go for either 80 or 100 amp RCD dont forget these are not overload devices they are RCD's basically an isolator with RCD protection
 

Reply to Melting rcd in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
620

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top