Hi lads
Can anyone help? I've wired a pv circuit to a mem cu 10 way it's tripping everytime some of the appliances are switched on
 
What's the make up of the consumer unit? RCD for all circuits, two RCD's for a number of circuits each?

Is the inverter suppied via an RCD which supplies other circuits?
It certainly sounds that way so leakage from the inverter coupled with leakage from additional appliances might be just enough to trip the RCD.

Something else to consider though - an inverter can take up to 5 seconds to disconnect. If it's supplied from an RCD which also supplies other circuits that rely on a disconnection time of 0.4 seconds then those circuits could potentially stay live until the inverter disconnects leading to a potentially lethal condition.
 
Last edited by a moderator:
Thanks for all the advise lads
I went there tonight to see if I could solve it and it turned out that the problem was on the hob, everytime the customer turned on the hob it tripped the RCD with all other circuits off including the pv circuit, all though it's weird after me installing it only yesterday! Is there anyone else here installing pv?
 
Did you see my point above about installing an inverter with an up to 5s disconnection time on a common RCD that shares circuits required to disconnect in 0.4s? It's dangerous.

Also, there's an excellent PV section on this forum.
 

Reply to Mem nightmare in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
932

Similar threads

M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K
  • Question
Did it work?
Replies
3
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top