Hi Guys
Just looked at a CU today and couldn't find a reference on a MEM 80A 30ma RCD ref:404ELHNC.
Anybody know what it would be - seems too old for 61008..
Tony
It'll probably be one of the old BS4293's then methinks. Remember the trip times on the 5x setting is 200ms instead of 300ms for a BS only device! :)
Not a problem. Remember that if this a front end RCD protecting the whole board and you're doing a PIR, then it should be coded as a 4 as in the event of any circuit having a fault the whole installation will trip out...
If not doing a PIR, then don't worry about it, although it's definitely something worth discussing with the client, :)
Reply to MEM RCD - What BS ref? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks