I installed a ringmain in an office flush in the wall in pvc conduit, tested the circuit and its over the max zs allowed for a type c 32a rcbo.
no prob i thought i will get a type b, after searching i cant get one, spoke to merlin gerin they said they dont make them, i said what if my zs is over max allowed for type c to table 41.3,
they said the max allowed is stated in table 41.5 which is 1667 i said no that refers to TT systems not PME system, they said no you can use that table for all zs reading, i then tried to explain about the other tables ie 41.3 and they said to ignore them and use table 41.5 again i said this refers to tt systems it even states about earth rods below the table.
basically that was the end of the conversation and told them i was going to speak to the niceic about it, which im yet to do as i couldnt get through on friday.
anyone else had these problems, with merlin gerin and what are your thoughts on the above.
thanks.
no prob i thought i will get a type b, after searching i cant get one, spoke to merlin gerin they said they dont make them, i said what if my zs is over max allowed for type c to table 41.3,
they said the max allowed is stated in table 41.5 which is 1667 i said no that refers to TT systems not PME system, they said no you can use that table for all zs reading, i then tried to explain about the other tables ie 41.3 and they said to ignore them and use table 41.5 again i said this refers to tt systems it even states about earth rods below the table.
basically that was the end of the conversation and told them i was going to speak to the niceic about it, which im yet to do as i couldnt get through on friday.
anyone else had these problems, with merlin gerin and what are your thoughts on the above.
thanks.