hi all

quick question , have an outbuilding which has no extrenuous conductive parts (water,gas,steel frame construction) the supply is TN-C-S and the earth has been extended to the outbuilding. The existing C.U. is plastic but has become damaged, are there any problems re earthing/bonding if a more robust Metal C.U. were to be fitted. i cant think of any or will the the new metal C.U. be classed as an exsposed conductive part and require bonding back to the M.E.T (10mm2) 0r am i confusing this with extrenous conductive parts

many thanks
 
You are confusing the two terms....an exposed conductive part is part of the electrical installation and requires earthing.
An extraneous conductive part is not part of the electrical system but may introduce a potential,usually earth,and may require bonding.
The metal case of a CU will thus be the former and require earthing
 
thought so getting my terms mixed up, brain slowing, the metal c.u is earthed via the tncs earth, and of course it is an exsposed conductive part so no bonding required, and as stated there are no extrenuous conductive parts.

just to check. Metal / plastic C.U makes no difference when exporting tncs earth?

when working on TT supply (rcd protection on tails) if metal C.U. is used?

as you here so many myths re taking tncs earth to outbuildings,
 
thought so getting my terms mixed up, brain slowing, the metal c.u is earthed via the tncs earth, and of course it is an exsposed conductive part so no bonding required, and as stated there are no extrenuous conductive parts.

just to check. Metal / plastic C.U makes no difference when exporting tncs earth? None whatsoever

when working on TT supply (rcd protection on tails) if metal C.U. is used? Or take precautions to ensure tails cant short out onto case...ie- bushing entry, DI tails,clamping to ensure no movement......100-300ma T/D RCD prefererred option.

as you here so many myths re taking tncs earth to outbuildings,.....Yep.....:banghead:


...........
 

Reply to Metal C.U (exsposed conductive part) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top