I 've been asked to do some work on a 1970s flat where the metal conduit is used as the protective conductor, How would I test the continuity of the ring circuits.Any help greatly appreciated.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Metal conduit as earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
a Maharg you have an old PME system
Prove the continuity of P-P and N-N
ensure all flyinf leads are in place and take a long lead round all the points to prove earth continuity R1&R2 then take the Zs on the points. As the Metalwork is the earth to many earth paths to mention so the ZS and Long lead is the clincher.
Alternitavly you could get a conduit tester and test the lot but if you do BE CAREFULL!!!!!!!!!!!!!!!
Trix
Sa for a conduit Tester it is a recognised tester which sends 25a throught the conduit to mrove the connection of the joints. Last time i saw one was when i was serving my time in 1990 but as it makes the containment live you have to be VERY carefull and it there is a loose connection in the conduit it could heat up like a toaster.
Thanks Scotsparky but this poses another problem.I recognised the PME supply distributors fuse but the main earthing has been disconected from the housing and clamped to the incominig supply conduit which is a copper enclosed in a sheath.The periodic test done last year has it marked as T-N-S.