Hi all,

Just wanted to ask a quick question.
My parents have nominated me to their friend (old couple) to swap 3 outside lights (original lights & new are metal) which they have purchased. Fine am happy to do it.
First light was done fine, all tests done.
The next light is a pir which also feeds the other light (none pir).
The issue is that there is no earth core just the black & red. Having a look at the cables feeding the light they are in the ceiling/floor void. They dont want to lift carpets & flooring etc. I advised them that the lights need an earth or they would have to change them for plastic ones which they said no to. So now i need to try & get an earth there to the light.
The cu is not a split load with no rcds fitted but it does have a external rcd fitted before the cu.

I have been asked if i could take an earth from a socket which is on the otherside of the wall or possibly the cieling rose? Eaither way the earth would then be on another circuit which im not happy with even though it would at least then be earthed.
What other options could anyone suggest that doesnt involve lifting flooring etc?


Thanks in advance

Michael
 
Hi all,

Just wanted to ask a quick question.
My parents have nominated me to their friend (old couple) to swap 3 outside lights (original lights & new are metal) which they have purchased. Fine am happy to do it.
First light was done fine, all tests done.
The next light is a pir which also feeds the other light (none pir).
The issue is that there is no earth core just the black & red. Having a look at the cables feeding the light they are in the ceiling/floor void. They dont want to lift carpets & flooring etc. I advised them that the lights need an earth or they would have to change them for plastic ones which they said no to. So now i need to try & get an earth there to the light.
The cu is not a split load with no rcds fitted but it does have a external rcd fitted before the cu.

I have been asked if i could take an earth from a socket which is on the otherside of the wall or possibly the cieling rose? Eaither way the earth would then be on another circuit which im not happy with even though it would at least then be earthed.
What other options could anyone suggest that doesnt involve lifting flooring etc?


Thanks in advance

Michael
If they don't want the fittings changed, and if they don't want you lifting carpets etc, then just tell them respectfully that you can't, fit the lights to comply with BS 7671, and walk away. It really is as simple as that. Explain the reasons why, it will be their choice as to the next move.
 
Can you not get double insulated light fitting(s)?

Hi Jamie,

They had already bought the lights they wanted me to fit.
If i had of been asked before they got them i would have popped over to check that the wiring had a cpc first.
 
If they don't want the fittings changed, and if they don't want you lifting carpets etc, then just tell them respectfully that you can't, fit the lights to comply with BS 7671, and walk away. It really is as simple as that. Explain the reasons why, it will be their choice as to the next move.

Hi Pete,

Thanks again for replying so quickly.
I have just called them to explain the options & have left it up to them to decide what they want to do next.


All the best

Michael
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Loki

Arms
-
Joined
Location
Devon
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Metal external lights but not earthed
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Loki,
Last reply from
Pete999,
Replies
5
Views
121

Advert

Back
Top