Hi, first time poster, long time lurker. Guess I'll have to start getting involved...
Just looking for some advice really on something I haven't come across before (I don't usually work on farms).
So I'm working on an installation that is TN-C-S (PME too) and I'm putting in a new TT sub-main to a metal container. Obviously TN-C-S is not preferred on a farm but that's "how its always been" and by the sounds of it / nature of the installation it hasn't caused any issues with animals.
When looking at the incomer I have noticed that the main earth doesn't have a MET and is just bolted into the metal casing; with other earths to sub-mains on the same bolt or bolted in close by. Continuity testing and EFLI is coming back ok suggesting no high impedance connections between these.
I have discussed complete isolation of supply to add in a MET but apparently this isn't an option.
Am I right in thinking this is not acceptable even though tests ok or would this be allowed?
If this is a departure what regulation would you list this under on the EIC?
Thanks
Shaun
Just looking for some advice really on something I haven't come across before (I don't usually work on farms).
So I'm working on an installation that is TN-C-S (PME too) and I'm putting in a new TT sub-main to a metal container. Obviously TN-C-S is not preferred on a farm but that's "how its always been" and by the sounds of it / nature of the installation it hasn't caused any issues with animals.
When looking at the incomer I have noticed that the main earth doesn't have a MET and is just bolted into the metal casing; with other earths to sub-mains on the same bolt or bolted in close by. Continuity testing and EFLI is coming back ok suggesting no high impedance connections between these.
I have discussed complete isolation of supply to add in a MET but apparently this isn't an option.
Am I right in thinking this is not acceptable even though tests ok or would this be allowed?
If this is a departure what regulation would you list this under on the EIC?
Thanks
Shaun
- TL;DR
- TN-C-S, Metal incoming supply cupboard used as MET. Departure or not? If so, which regulation?