Afternoon all,

Carried out an EICR yesterday, on the job I doscovered the consumer unit to be located in the kitchen and the incoming supply under the stairs. The tails feeding the board look to me to be just over 3 meters perhaps 3.5. But it is difficult to tell as they are ran in an internal wall.

What coding is recommended and what remedial action required.

Im thinking C2 with a fuse fited between the isolator and the consumer unit.

Cheers

Dave
 
i wouldnt be coding anything unless one can confirm the tails are indeed greater than 3mtrs rather than a rough estimation on a cable route you cant see.

and its a C3 at worst if the tails are current rated above the dno fuse size.

that said , no rcd protection for cables hidden within the fabric of the wall without earthed mechanical protection would probably warrant a C2.

and reg 433.2 doesnt apply to CU tails as there is no reduction in cable size along its path from meter to CU.

so im still not convinced the issue is within the remit of an inspection conducted to bs 7671 to begin with......
 
Last edited by a moderator:
A number of people believe that 433.2 and 434 do not apply in these instances.
I do not understand why people have this belief, as they must be aware that the distribution network does not fall within the parameters of BS7671?
I believe that this has promted the network distributors to now insist oversized conductors of 25mm be installed.
There does appear to be a misconception that the network operators protective device is intended to provide protection for the installation, however in fact it is there to protect the network operator's equipment.
It is very rare that the network operators will agree for their device to be used to protect an installation, when they do allow such, they impose quite severe restrictions and conditions.
From BS7671's view point the installation begins at the Meter, and any protective device upstream from the Meter is of no consequence.
As such, if the Meter Tails are longer than 3m, a protective device is required along that run.
The OP has also indicated that the tails are run in a cavity wall, which is something the network distributors do not allow.
 
A number of people believe that 433.2 and 434 do not apply in these instances.
I do not understand why people have this belief, as they must be aware that the distribution network does not fall within the parameters of BS7671?
I believe that this has promted the network distributors to now insist oversized conductors of 25mm be installed.
There does appear to be a misconception that the network operators protective device is intended to provide protection for the installation, however in fact it is there to protect the network operator's equipment.
It is very rare that the network operators will agree for their device to be used to protect an installation, when they do allow such, they impose quite severe restrictions and conditions.
From BS7671's view point the installation begins at the Meter, and any protective device upstream from the Meter is of no consequence.
As such, if the Meter Tails are longer than 3m, a protective device is required along that run.
The OP has also indicated that the tails are run in a cavity wall, which is something the network distributors do not allow.

section 433.3.1 (iii) says that overload protection may be omitted where a service fuse is agreed to afford protection to any run between it and the main distribution point of the installation. i.e. the cable CCC exceeds that of the service fuse.
 
Yes, when it is agreed.
If it has been agreed then there will be a written agreement with a list of conditions and stipulations as long as your arm.
I doubt very much that such an agreement would be made for a domestic installation, where there are no statutory requirements for who has control of the installation.
 
Last edited by a moderator:
Yes, when it is agreed.
If it has been agreed then there will be a written agreement with a list of conditions and stipulations as long as your arm.
I doubt very much that such an agreement would be made for a domestic installation, where there are no statutory requirements for who has control of the installation.

I think it's agreed with our DNO then. I asked them about this recently and they had no knowledge of any 3m rule or any stipulation for fusing of tails of any length.
 

Reply to Meter Tail Length in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
672
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top