Hi

Has anybody ever found where this "rule has come from"? In the NAPIT codebreakers book it quotes "ESQCR regs" but it is not actually written in there. If it is a DNO rule then it comes under their regs (ESQCR), but as I said, it is not in there....
 
I think different DNOs sometimes have slightly different requirements, but the 3M rule is a good rule of thumb and should ensure compliance.
 
It’s the DNO’s fuse for protecting their equipment, not for protection of the consumers side, other than what they allow which is typically 3 meters.
Not that they police it mind.
I also wouldn’t code it on an EICR tho for tails longer than this, provided that the fuse offered fault protection.
 
DNO requirements
It's important to remember that their 'requirements' are nothing more than 'nice to haves'. We have no legal or moral duty to comply with them.

I would take a far more case by case approach to the provision of isolation on tails rather than trying to stick religiously to a 3m preference expressed by companies who ultimately have no duristiction over anything past the main head.
 
It's important to remember that their 'requirements' are nothing more than 'nice to haves'. We have no legal or moral duty to comply with them.

I would take a far more case by case approach to the provision of isolation on tails rather than trying to stick religiously to a 3m preference expressed by companies who ultimately have no duristiction over anything past the main head.

I'm not saying you should necessarily stick to it 100%, I was saying it could be a rule of thumb guide to what DNOs sometimes require
 
I believe is DNO rules but not written in stone
This is how it is written in the NAPIT Codebreakers book. If it is "ESQCR" then why is it not listed in there?? How can it be a DNO rule if different DNOs quote different lengths? Here in the westcountry, WPD will not allow sparks to remove the service fuse but in the east of the country the DNO permits it!
 

Attachments

  • [ElectriciansForums.net] Meter tails >3 metres in length
    Capture.JPG
    21.5 KB · Views: 44
Why would you FI that?
What limitations during the inspection would lead you to believe that there could be potential for danger but a limitation on the inspection prevents you from finding out?
Then they quote the ESQCR ?
 

Reply to Meter tails >3 metres in length in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
857
  • Question
It sounds like the original meter was reading incorrectly and octopus aren't keen to admit this as they would probably have to refund you. I...
Replies
1
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top