Hi guys,
Been to a one bedroom retirement bungalow today, supply is tncs into a cupboard just outside the front door, it goes into a 63a isolater then it goes from there into the roof void and into the consumer unit which is approx 6 meters from the isolater. The board is supplied via 16mm t+e with a 6mm (or perhaps 4mm) main earth. The ze was .50 which is obviously too high, I have now installed a 16mm main earth and the ze is now .38 which I am aware is still a fraction too high. My question to you all, is I am right in saying that the old earth was too small as I'm sure that it should be at least half the size of the meter tails.
They had another more experienced electrician do a pir a couple of weeks ago and he didn't mention it.

Im sure I'm correct in what I'm thinking, but you know what it's like, doubt starts to kick in and I would love to hear what you think.
 
As above, I'd imagine the ze at source to be highish..... Plus another 6meters, tipping it over.

id agree that the 4mm was easily too low, 10mm minimum IMO....
 
TNCS minimum Ze is 0.35ohms. If it's outside this you need to inform the supply company to investigate.
TNCS requires a minimum of 25mm tails and 16mm earth conductor.
 
Right, you've got a Zdb of 0.38.
That equates, (roughly, depending on actual voltage) as a PFC of 460A
What is the cut-out fuse size?
Is it a 63A as you stated, or is that an isolator?
So, assuming it is a 63A BS88-3, it will trip in one second - is this a homework question, as 460A is right there on page 296.
Do the adiabatic, and you get a 4mm earth conductor.
But then you need to cross-reference to 544.1.1 which states that a 10mm earth conductor is the minimum for a TN-C-S (PME) system.
So 10mm is required.
However, is the main earthing terminal in the CU, or at the isolator?
 

Reply to Meter tails and main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
514
You would treat it as a TT installation.
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top