thenugnug

Hi there i have a metrel easi test one of the new ones and have had something come up today which i have never seen before. The symbol was an arrow going in the floor which i have now found out is "phase voltage on the PE terminal",could someone explain this as the installation works fine and there appears to be no voltage on the PE,please help,thanks
 
Yes - the way the Metrels test for a high touch voltage on the earth connection is thru your finger to earth. The better you are grounded the more likely you are to see this warning, which is usually just annoying but may save yer life oneday.

To check, try pressing test with an insulated screwdriver handle or the like, the warning should not appear.
 
Last edited:
mine does this all the time, i think it's a fault. it's always when i'm doing zs at a light fitting, never when i have the plugtop lead in doing zs at sockets. it comes up with the warning as soon as L and E terminals are on.
 
mine does this all the time, i think it's a fault. it's always when i'm doing zs at a light fitting, never when i have the plugtop lead in doing zs at sockets. it comes up with the warning as soon as L and E terminals are on.

actually, it does it as soon as my thumb touches the bloody test button! tried it using a spare insulated probe and it works fine. can't beleive i've been getting error messages for weeks now and all i had to do was press test with something insulated from me. there should be a warning in the handbook that explains this.
 
I've just had the same thing happen, so thanks for posting.

actually, it does it as soon as my thumb touches the bloody test button! tried it using a spare insulated probe and it works fine. can't beleive i've been getting error messages for weeks now and all i had to do was press test with something insulated from me. there should be a warning in the handbook that explains this.
 

Reply to Metrel easi test,strange readings in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
980
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
370

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top