I did originally post this in the Tools and Products area - but think that was probably the wrong place.

Recently, I purchased a Metrel MI3000. The initial impression was actually very good - looks robust enough and with very logical controls.

Shortly after getting it and whilst installing a SWA run to an outbuilding through a RCD spur, I had my first opportunity to test the No Trip PEFC facility. The readings were much higher than I expected (about 2 Ohms!!) so much re-checking of connections ensued, followed by another test - readings exactly the same. It's worth pointing out that the automated PSCC readings from the socket in the outbuilding were spot on.

My gut instinct is that the No Trip process is probably giving the unexpectedly high reading, so I took the meter into the house and tested from a socket adjacent to the spur (fed from the same ring). This seemed to confirm suspicion - no trip reading was almost exactly 1.5 Ohms higher than the standard (this socket is not RCD protected, so could perform both tests on it back to back). Reading with the No Trip facility set was 1.94 Ohms (so, that would be outside limits for the 32 A Type B breaker protecting the ring). However, with the No Trip facility switched off, the reading was a much more acceptable (and realistic) 0.43 Ohms.

So, long-wnded question, but can anyone throw some light on this for me? Until I've got it sorted, I'm definitely not going to trust the No Trip readings on this meter.

Cheers.
 
hope you mean Zs, not pefc when you say ohms. the bad reading could be caused by noise on the circuit. i would deffo be on the phone to metrel, as it's under warranty.
 
hope you mean Zs, not pefc when you say ohms. the bad reading could be caused by noise on the circuit. i would deffo be on the phone to metrel, as it's under warranty.
DOH! Yes - a slip of my best typing fingers (and inability to proof read!)Thanks for the advice - and correction (embarrassed!)Cheers,Ian.
 
RCDcould well be the problem. i tested a job recently where Ze was 0.2. the Zs read 351! retested at CU busbar and still got 349. a lot worse than your discrepancy.
 
Thanks very much for the replies Telectrix and Tony MC. I do suspect that the RCD is playing a part in this.

I suppose that RCDs, by their very nature, would introduce resistance.

Thanks again,

Ian.
 
There was a thread on here a while back about Megger doing the same thing, giving un-realistic readings on the no trip facility, and I believe megger upgraded the MFT free of charge to stop this, but as usual can't find the thread.

As the meter is new I would still contact metrel and tell them what is happening and see if they offer you the same solution.
 
Were the batteries on the Metrel low? I've noticed that if mine are low "unusual" readings can result, recharge the batteries and readings become "normal"!
 
Thanks Murdoch - had not thought of that. The batteries were about half charged, but I will give them a full charge and see if it improves the readings.
 

Reply to Metrel MI300 - Unexpected No Trip Zs Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top